wiring boiler/ergomax in my situation


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #2 ] [ FAQ ]

Posted by Dave on February 05, 2006 at 00:37:28:

Well, we piped in the ergomax into my system and had 1 problem. The Taco 0010 was actually pumping boiler water through all our supply pumps in the header even when the pumps were not running so that all zones were very hot at all times.
I spoke with Adam at Ergomax/Group Thermal and he recommended repiping as follows:
We kept the primary/boiler loop the same (boiler water enters top of Ergomax and water returns to boiler from bottom of ergomax through 0010 pump that pumps into boiler).
Adam told us to put supply and return headers as 2 closely spaced tees off the return from ergomax to boiler which we did about 3 feet from tank.
We found that 0010 pump must now run whenever any zone is calling for heat, as individual pumps will not pull hot water into zones unless boiler pump is operating.
This creates the following problems:
1. When I had ergomax alone wired across TT on boiler, we had the situation where the tank called for heat after our other zone pumps had shut down and boiler locked out as there was no boiler pump running. (boiler pump was wired through Taco SR504 to run only when individual pumps were running).
2. I removed ergomax aquastat connections on boiler and wired the TT terminals on boiler to endswitch on Taco SR504. So any zone could call for heat from boiler. However, if the system was idle for a while so that boiler cooled down and then a zone called for heat, even though ergomax was 160 degrees, the boiler immediately started because the water in it was cold. Boiler operating temp is 175 and high fire is 160. So if boiler had cooled down substantially and then a zone called for heat, boiler pump would come on as inlet temp was about 120 and boiler would fire even though relatively quickly it was seeing 150 degree water flowing through it.
What would be the best way to make this situation more efficient? I would like boiler to be controlled by aquastat from ergomax only. And the boiler pump needs to run when either boiler calls for heat, or any individual zone runs.
I am not against getting rid of SR 504 if something else would work better.
I was thinking....would it be possible to treat the aquastat on the ergomax as a thermostat input on the SR504, then I would add another low voltage wire that goes parallel from the ergomax input on the SR504 to TT on the boiler? Then, the ergomax would run the boiler pump whenever it called for heat as well as fire the boiler and also the zone pumps would also run the boiler pump as needed?
Would heatmanager work well also in this situation?
Thanks.