Re: Getting boiler to operate more efficiently


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #2 ] [ FAQ ]

Posted by Joe Brix on November 16, 2005 at 15:45:00:

In Reply to: Getting boiler to operate more efficiently posted by Justin on November 16, 2005 at 14:32:14:

If you have an outdoor reset control, your boiler should not be hitting the high limit. An O. Reset should only allow the boiler to get to max temp on the coldest days of the season. Even without a reset control, the burner should stop once a thermostat is satisfied. Sounds like something is not wired right, or the aquastat is set wrong.
DOes the aquastat have a low limit thats been turned up too high with a a wide differential set so it runs to high limit all the time?