Do the entire test procedure to isolate problems:
When a tech uses combustion test instruments to give you a complete combustion test list including the data for:
Oil nozzle pressure ____
Pump suction pressure _____
draft over the fire _____
draft in the fire chamber ____
No smoke setting ____
CO2 percentage ____
room temperature _____
Stack temperature _____
Combustion efficiency _____

Then he will have a starting point to know, after all parts are clean and set to factory specs, if a condition like inadequate draft or other problem is a cause. If he doesn't have or use these instruments there is little chance that the burner will be adjusted to prevent soot or be so wide open that oil is wasted.

http://www.heatpro.us/service/oilserv.htm