Re: Triad Boiler Air Purge


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #4 ] [ FAQ ]

Posted by Dan on November 03, 2010 at 09:06:31:

In Reply to: Re: Triad Boiler Air Purge posted by HeatPro on November 02, 2010 at 19:15:56:

Thanks so much HeatPro. I will look over all the information that you have pointed and give it a try over the next few days. I might come back with a follow-up question if I am not successful in getting the purge done correctly. Thanks again!

: :Purge each of those 5 zones with the other zone valves closed, one-by-one with the spigot valve opened, then closed for each one. Then purge the line from the feed valve to the spigot with all zones closed off.

: Read over the purge instruction here,
: http://www.livepast60.com/heatpro/purgeairtree/documents/D5F0F0F6AB134840F7ADDA6F136ED396F851F932.html

: to see the difference between purging with the older tank or with the newer diaphragm tanks, as they make a difference. You don't want an auto-vent with the older air-control tanks that don't have the diaphragm.