Re: Honeywell Aquastat L8148A - Lowering setpoints


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #4 ] [ FAQ ]

Posted by HeatPro on May 07, 2009 at 11:26:31:

In Reply to: Honeywell Aquastat L8148A - Lowering setpoints posted by Mr Bag-O-Beans on March 18, 2009 at 18:58:43:

: Can the temps be made lower than 180 deg. , for summer use. I only use it for DHW heat with a Boilermate. And if not - Why?

The setpoint of an L8148A is the high limit temperature. By moving that lower you assure that the water of the boiler is kept lower, which translates to having the burner go on and off several times to make the hot water. As indirect tanks make the hot water at their rating (often 170F into the tank exchanger, you are assuring that the burner will go on and off more often and the water in the tank will take longer to heat.