Re: peerless boiler soot problems


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #4 ] [ FAQ ]

Posted by Rick on December 12, 2008 at 01:38:30:

In Reply to: Re: peerless boiler soot problems posted by rbeck on December 07, 2008 at 09:23:51:

: : I would start with combustion air and gas pressure. If this is new check orifice sizes. This is a very dangerous situation. It should not be run until resolved.
: : To calculate combustion air see the link below. Sorry no link in last post
: http://www.comfort-calc.net/Combustion_Air_Calculation.html
The boiler is in an open unfinished basement, that is damp and dirty all the time. Gas pressure in the manifold is 3.5 w.c. Does the gas pressure need adjustment higher or lower in the smartvalve?
What about a draft inducer, or dropping vermiculite around the chimney liner between it and the brick?