Re: BOILER


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #3 ] [ FAQ ]

Posted by pete on December 14, 2007 at 05:29:27:

In Reply to: Re: BOILER posted by HeatPro on December 13, 2007 at 22:46:21:

: If it has no low limit control, so is a 'cold start' boiler as many are today, then it needs no low limit. The single control with the dial would be a high limit (usually an L6006A) to prevent the boiler from getting too hot.

: As you have more than one zone, the boiler water will rise to the high limit setting approximately, due to one zone, then another calling for heat repeatedly.

: If you want the boiler to reise to temperatures as needed then
: http://www.taco-hvac.com/en/products/PC700+Boiler+Reset+Control/products.html?current_category=150
After a cold start, (when call for heat)And one or more zones are calling for heat the boiler always restarts at about 180 degrees to 190 degrees until heat where needed has been satisfied, if that is a shut off switch only for max. temp of boiler setting, what makes boiler kick back on at that 180- 190 range when heat is being called for like something is set at that temp.? It cant be a coincidence it kicks on at that temp everytime. It seems to me the honeywell aquastat has a 15 degree differential from the set point you make it? Like set at 195 degree would give you a 210 degree shut off and a 180 degree kick back on.(allow power to flow)