[an error occurred while processing this directive]

Re: Boiler Low Limit Question


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #3 ] [ FAQ ]

Posted by HeatPro on November 21, 2007 at 09:51:38:

In Reply to: Boiler Low Limit Question posted by Gary on November 21, 2007 at 00:58:46:

You state that you want the circ to run til the low limit is met, as an L8148A doesn't have one; you'd need a 60 to have one. It is also odd that the circulator runs for 15 seconds after the burner shuts off as an L8148A cuts them both off at the same time. A low limit would keep the boiler hot which is what you don't want. What you are looking for is a Peerless or System 2000 control to send the hot water out of the boiler to the radiation after firing or, as suggested, wire the circulator to run all the time.


Follow Ups:



Post a Followup

Name:
E-Mail:

Subject:

Comments:


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #3 ] [ FAQ ]