The first problem is that the safety relief valve blows at 5 psig. If you have a PRV on there, it is the wrong valve. A working safety relief valve on a hot water system would pop near 30 psig. A steam relief valve would pop at 15 psig. Whichever system you have they should lift at those pressures and not 5 psig. It is more likely that the pressure gauge is way off and that needs replacement too. Test the pressure with a known-good gauge.

If your system is a steam system, (this is a steam forum) then there wouldn't be an expansion tank in the system.

If your system is a water system then it should never get hot enough to spray steam. The water temperature would have to be over 230F to spray steam from a 5 psig system, which means the high limit would be mis-set.

Whatever the situation, get a pro in there who can tell the difference between a steam system and a water system and know what things should be doing. It isn't a good idea to try to fix a machine you don't have a clue about.