HeatSponge Boiler Economizers "Saving The World From High Fuel Costs" Natural gas will never be inexpensive again making a boiler economizer more important than ever. HeatSponge offers products for boilers ranging from 50 HP to 150,000 pph. Improving boiler efficiency results in reduced pollution levels. Check how much money you can save by visiting our website. Click Here For On-Line Performance and Pricing. |
Posted by rep on February 18, 2006 at 00:01:47:
I have an old Kewanee Type R Model 1736 that is rated at 700 SF/EDR and was told this unit will run at 80% efficiency. I realize it’s oversized but as it is seldom used I have no plans to replace it. I would like to increase the efficiency if I can. I suspect the burner is over firing.
Would the following calculation represent the amount the burner could be over firing?
700 SF/EDR Gross Output x 240 BTUH per SF/EDR (steam) = 168,000 BTUH Rated Gross Output at 80% efficiency.
168,000 BTUH divided by .8 = 210,000 BTUH Rated Input (estimated)
Current Firing Rate of 270,000 BTUH (clocked the gas meter) – 210,000 BTUH Rated Input = 60,000 BTUH amount of over firing per boiler rating?
The load on the boiler is about 68,330 BTUH for the radiators and 57,000 BTUH for the piping.
I need to understand what’s involved so I can recommend and monitor what the technician does.
1. To down-fire by 60,000 BTUH would I change orifice size or something else?
2. Would the manifold gas pressure need to be adjusted?
3. If I did down fire it by 20-25% would it run 20-25% longer to heat the radiators?
Thanks