Re: Relocating circulator due to air problems. Need help


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #2 ] [ FAQ ]

Posted by HeatPro on August 23, 2004 at 15:23:00:

In Reply to: Relocating circulator due to air problems. Need help posted by Richard on August 22, 2004 at 16:48:32:

The installer almost 'got away' with the old-timey installation of the circulator on the return; it is not the best way.

Don't reverse-flow the boiler, you can have noise and other problems.

If you must, add a horizontal loop at the supply side to extend the piping to get the circulator pumping away from the expansion tank. You could turn the supply piping with the expansion tank on it in the other direction, then come back with the room to install the circulator.