Re: fireye connections


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]

Posted by Steve Jeppesen on November 02, 2006 at 11:23:16:

In Reply to: Re: fireye connections posted by sid on October 10, 2006 at 21:21:36:

: :I would say it is their to test the fireeye . You do test you safety controls a least once a year i hope.

I would remove it. I have never heard of any one installing a valve on the cooling nipple to the Fireye. As far as the ALWCO, LWCO & the GG's, these SHOULD be blowdown/tested once every 8 hours while the boiler is in operation. The Fireye may be tested every 8 hours also, but can be tested once every week. The evaporation test and the MTFI are monthly tests. I HOPE YOU ARE NOT TESTING ONCE PER YEAR!!!!!!!!! If you are you are looking at a possible boiler explosion.