HeatSponge Boiler Economizers
"Saving The World From High Fuel Costs"

Natural gas will never be inexpensive again making a boiler economizer more important than ever. HeatSponge offers products for boilers ranging from 50 HP to 150,000 pph. Improving boiler efficiency results in reduced pollution levels. Check how much money you can save by visiting our website. Click Here For On-Line Performance and Pricing.




Re: Running Circlulator w/o Running Boiler


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #3 ] [ FAQ ]

Posted by HeatPro on December 31, 2007 at 18:58:11:

In Reply to: Running Circlulator w/o Running Boiler posted by Wagner Family on December 31, 2007 at 18:15:26:

Two zones - will also need to open the zone valves, but I can do that manually of needed.

The 8124 control is there to keep the boiler warm so you can have hot water available. To keep the circulator running, you'll need to disable the low limit feature - not that simply done without other complications. You could run two wires from the oil safety relay TT terminals, removing the jumper there, and run the wires upstairs to a switch to keep the burner off while the thermostats call for heat from the zone valves. All would work to open the zone valves with the thermostat and start the circulator without the burner running until you closed the switch again.




Follow Ups:



Post a Followup

Name:
E-Mail:

Subject:

Comments:


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #3 ] [ FAQ ]