Natural gas will never be inexpensive again making a boiler economizer more important than ever. HeatSponge offers products for boilers ranging from 50 HP to 150,000 pph. Improving boiler efficiency results in reduced pollution levels. Check how much money you can save by visiting our website. Click Here For On-Line Performance and Pricing.




Re: wiring up my Taco SR504 relay..........


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #3 ] [ FAQ ]

Posted by Craig on December 19, 2007 at 11:23:24:

In Reply to: Re: wiring up my Taco SR504 relay.......... posted by HeatPro on December 16, 2007 at 17:39:03:

: It can get confusing with the rare once-in-a-lifetime experience.

: All of the end switch wires of the Honeywell zone valves go to the one place on your present wiring, so that one place in the wiring is where the TT to the left of the SR504 picture goes
: http://www.houseneeds.com/Shop/manuals/taco_sr504manual.pdf

: All the thermostats go to the Zone 1, Zone 2, Zone 3 as shown up top. The wires from the 4th zone thermostat just go to Zone 4 terminals up top.

: In other words, when you transfer all the thermostat wires from the 3 zone valves (and one from the transformer,) what's left are the two wires on all the zone valves that lead back to the boiler wire location that starts the burner - that goes to TT on the SR504.