Pressure settings


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Steam-Forum ] [ FAQ ]

Posted by jtown on January 17, 2000 at 06:53:31:

In Reply to: Re: Pressuretrol keeps cutting out posted by Joe on January 16, 2000 at 16:26:15:

You want as low a pressure as possible. Look in the cover of your pressure switch. There should be a label that tells if the differential is additive or subtractive. The reading on the wheel is added or subtracted from the pressure setting. Some people will have two scales on the front, one being differential. Set your pressure to the minimum and your differential for 0.5psi and give that a try. The pressure will rise to the higher pressure and the burner will "cut-out" and then the pressure will drop to the lower and the burner will "cut-in"