Posted by Nader Mirzaee on April 05, 2004 at 00:11:18:
In Reply to: Re: safety valve fittings posted by Joeblack on November 24, 2002 at 19:11:49:
: : There is no code violation reducing the boiler connection down to the safety/relief valve inlet diameter, BUT NOT LESS than the safety/relief valve inlet diameter. If the valve is leaking give it a few blows with the hand release lever, be careful you don't get burned, if that does not work replace the valve.
: Thank you, this helps alot.