[an error occurred while processing this directive]

Re: cleaver brooks fault [ #28-#29 ]


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]

Posted by ted tobey on February 28, 2012 at 07:50:33:

In Reply to: Re: cleaver brooks fault [ #28-#29 ] posted by earmic on December 17, 2011 at 08:56:17:

: : we are getting fault #28 and prior fault #29.
: : both lock out boiler and are combustion errors,
: : fault #29 is for pilot, I want to start metering out circuits / relays but isnt there a quick way to go strait to that particulare interlock and go from there ?
: : our manual is a little iffy due to we now have the new [ hawk paenl ] which display a different fault code but if your lucky and catch it the fault codes for the 28-and 29 will appear on top of screen [ before ] acknowledging.
: : any advice will be appreciated. [ I know to start checking out the pilot etc---but usualy ise a quicker componet to check , relay etc---

: Tell me more about the model of this panel, the boiler and fireye type. I might be able to help.

A common problem with CB boiler pilot flame failure is a dislodged burner drawer gasket. When gasket is out of place uncontrolled air flows to burner and may blow out pilot. If boiler does get lit off you will see a high O2 reading (over 15%) and a small, sharp, noisy fire. Gasket is easy to replace.


Follow Ups:



Post a Followup

Name:
E-Mail:

Subject:

Comments:


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]