[an error occurred while processing this directive]

Re: leaking burner housing


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]

Posted by sid on May 28, 2007 at 17:18:07:

In Reply to: Re: leaking burner housing posted by James on May 25, 2007 at 22:55:50:

: : :
: : : the burner housing on or cb 500 hp boiler is leaking gas around the burner we have had the same trouble on or 700 hp .cb says that the gas pressure is so low it is not necessary for this arer to be sealed . Like so input

: : No gas should ever leak from around the burner housing if the burner is set up correctly with the designed backpressure on the burner at maximum firing rate.

:
: Are you sure it's a gas leak or is it just combustion air? On a CB like yours the gas is well contained until the combustion chamber.




Follow Ups:



Post a Followup

Name:
E-Mail:

Subject:

Comments:


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 4 ] [ FAQ ]