[an error occurred while processing this directive]

Re: Unforseen problems with converting to natural gas


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 3 ] [ FAQ ]

Posted by Charlie on June 20, 2005 at 10:36:35:

In Reply to: Re: Unforseen problems with converting to natural gas posted by Tony Conner on June 19, 2005 at 11:46:51:

: If the retro-fit gas burner is properly selected & installed, you will have no problems, and I doubt that you'll see much change in efficiency one way or the other. I have worked in plants where the maximum boiler steam output would be different when firing bunker oil, or natural gas, but that was due to differences in the actual burner capacities. If you can make, say, 10,000 #/hr steam when firing oil, then there's no reason why you can't do the same firing gas, with no measuable impact on boiler efficiency, as long as it a proper installation. After that, the difference is what you're paying per BTU of fuel. Oil suffers a bit from needing to run pumps, usually requiring a little more fan power, and having to blow soot.

: Do you currently have separate fuel meters for each boiler? Do you currently have properly & pressure compensated steam meters for each boiler? If not, then you really don't know what your boiler efficiency is now, let alone what might change with a fuel conversion.

Thanks for your reply, Yes I do have separate fuel meters for each boiler but I don't have steam meters, The only way I would know if I wasn't keeping up would be if all boilers are at full throttle and I can't maintain 120psi steam.At the begining of our season I have a company come and do stack tests and come up with the efficiency burning #4oil plus emissions. Really the main thing is just keeping up without costing more than the #4 oil. Thanks again for the input.


Follow Ups: