Re: PITTING ON TUBES


[ Follow Ups ] [ Post Followup ] [ Boilerroom.com Steam-Forum - Number 2 ] [ FAQ ]

Posted by Allan Greene on November 13, 2001 at 15:49:22:

In Reply to: Re: PITTING ON TUBES posted by Ron on November 07, 2001 at 18:45:42:

: : : JUST OPENED A BOILER THAT WAS FULL OF WATER ,IT HAD BEEN IDLE FOR 1 1/2YEARS HAD BEEN TOLD IT HAD BEEN RETUBED 1YEAR EARLIER ,NOW IT HAS PITTING ON THE TUBES ,RESULTING IN TUBE LEAKS ,POOR LAYUP TO BE THE BLAME ? NEED SOME CURES TO THIS SITUATION AS IT IS GOING TO BE DIFFICULT TO DEAL WITH THANKS

: When we lay up our boilers, we keep them pressurized with 175# steam, with the condensate removed through steam traps on the open blow down lines. We can recover the condensate that way. When laying up the boilers, we open the drum vent until we get about 50# pressure to remove the air, since oxygen causes the pitting.

:There are two options, wet layup or dry layup, when you wet lay up you should fire your boiler (dry out) then chemical treat your feedwater in the boiler with a recommended dosage from a chemical company (depending on water volume) then apply a nitrogen cap to the boiler (ensures all oxygen is removed), The dry lay up basically consists of a dry out fire, draining the entire boiler then inserting a dessicant in the drum or water space of the HRT boiler. Hope this helps