Re: triangle tube boiler and pump


[ Follow Ups ] [ Post Followup ] [ Boiler Room Residential and Home Forum #4 ] [ FAQ ]

Posted by HeatPro on April 04, 2011 at 10:39:06:

In Reply to: triangle tube boiler and pump posted by Bisseti on April 04, 2011 at 07:54:51:

I suppose you calculated your head loss to be 30 feet because you either:
added up the total feet of tubing
or
added the height of the building to the loop length.

It's unlikely that a primary loop to move 100,000 btuh or 5 gpm of 1 inch would be long enough to require 30 feet of head. Recalculate.
As the Grundfos is a 3-speed, it won't make much
difference, as it can be set at low speed to handle the low head required.

Otherwise, you've given the 'apple' of what Triangle Tube has told you to do, but you haven't given the 'orange' of what other layout you propose to use. The safest way to get good operation without whining noises, and keep the warrantees on the equipment, is to follow the manufacturer design 'to the letter.'